Bathroom convenience receptacles must be gfi-protected. Water heaters typically are not. For the sake of discussion, would you REQUIRE the water heater receptacle pictured to be gfi protected? It is well below the sink, and there is another receptacle adjacent to the sink.
Would your opinion be affected if the WH receptacle was inside a cabinet?
- John Steinke
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Yes John, I would require that a GFCI was put on any outlet in a bathroom, regardless of wether it was in a cupboard or not.
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
NEC says "All" bathroom receptacles.
|
|
|
|
Joined: Jul 2004
Posts: 41
Member
|
Kenny Wilee
|
|
|
|
Joined: Jan 2002
Posts: 119
Member
|
I'm with everyone else here, the NEC says if the receptacle is in a bathroom, it "shall" be protected by a GFCI.
Although there probably isn't one... I would look for an alternative location for that WH.
|
|
|
|
Joined: Aug 2001
Posts: 335
Member
|
GFCI. There is no exception for a dedicated receptacle for a specific use item in bathrooms (like there is in garages for that extra freezer).
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Is it OK to cord and plug connect a water heater?
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
If it was in a cabinet....
AND a single outlet receptacle (like the exceptions listed in the Code)
Then maybe.
The way it is now (accessible & duplex)?
Not a chance.
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
"Cal-rod" metal-sheathed heaters and GFCIs can be a troublesome combination. Replacement of the cord and lower receptacle with fixed wiring might make better sense.
|
|
|
|
Joined: Aug 2004
Posts: 42
Member
|
" Should" be wired.....
Recessed single gang box, single gang, water proof extension box with sealtite, strapped and connected directly to Water Heater.
No GFCI
|
|
|