Administrator Member
|
The attached photos show telephone cable installed in such a way as to make me forget what I was doing and overlook for a time the supports missing on cables. If anyone recognizes the location, please do not state where it is. I asked permission to post these pictures as long as I did not say where they were taken.
1- The flexible conduits (and cables) need supports within 12" of the cabinets and at 3' intervals thereafter across the deck. NEC 350.30, 356.30
2- The flexible cable connection to the receptacle box is damaged and requires support as above. NEC 350.24
3- I should have checked the telephone cabling inside the hose, it must be listed for a wet location. The raceway (garden hose) is not listed for its use. NEC 800.4, 110.3(B), 800.6
4- The receptacles were GFCI protected by a breaker, but the cover was needing to be weatherproof while-in-use. NEC 406.8 (B)(1)
Shane
|
|
|
|
Joined: Apr 2004
Posts: 812
Member
|
No, no way... definately no way... Please tell me when the NEC said "Garden hose is a permitted raceway?" (Question not comment.) At least you can do what I know somebody said in another post, "Saving materials by combining water and electrical service." I'd like to see that hose connected to a faucet...