#117848 07/10/04 11:19 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Quote
Got a call to a loss of power in a couple bedrooms.... Went & checked the panel & things didn't seem to fit right... Someone gutted an old (Murray?) panel & stuck the guts in this former Zinsco panel... Problem traced to a deceased backwire Slater outlet in the bathroom... Repaired a broken hallway switch while I was there...

-Randy
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

#117849 07/10/04 11:20 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

#117850 07/15/04 03:54 PM
Joined: Apr 2004
Posts: 36
S
Member
looks like someone went through alot of un necessary work in this panel. It even looks like Square D breakers have been put in. Well i guess there needs to be some GE parts and maybe some FPE and Pushmatic parts to be totally mixed up. [Linked Image]

#117851 07/15/04 04:14 PM
Joined: Nov 2003
Posts: 269
E
Member
In pic 6, what is that white wire caught under a screw on the neutral/bond bar? Was there no other place for it?


John