ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 483 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
This is often seen where a cable has been cut and must be joined back together or someones' idea of Tapping into a line.
Why is this Bad?

[Linked Image]

Joined: Aug 2002
Posts: 25
J
Member
Back wrapped ECG's and short conductors, exposed hots behind wire nuts. Could have been done with 2 junction boxes spread apart with 2 new pieces of NM to give adequate wire for the 3-6 rule.

[This message has been edited by Joule-E (edited 09-22-2002).]

Joined: Nov 2001
Posts: 745
M
Member
Violations not withstanding, which Joule-e has already mentioned, this thing must have been VERY difficult to put together! [Linked Image]

Mike (mamills)

[This message has been edited by mamills (edited 09-22-2002).]

Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
assuming 1.5"x4" Octagon box and 14 AWG.
15.5 cubic inches / 2 Cu.In. = 7 14 AWG.

314.16.

4 - 2/C NM = 4x2 = 8 x 2Cu.In. = 16 Cu.In.

4 EGC's = 1 EGC = 2 Cu In.

4 Connectors = 1 connector = 2 Cu.In.

Total Cu.In. = 20 Cu. In..

Box is 4.5 C.In too small.

Plus 250.148(A).

Also looks as though some bare Ungrounded conductor exposed at the wirenut, possible 110.7.

Question 334.24.

Appears box was secured to the wood or maybe just a shadow over the bottom hole of the back of box.

[This message has been edited by Gwz (edited 09-23-2002).]


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5