ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 215 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 2,749
Member
[Linked Image from nachi.org]

1
2
3
4
5
6
7
8
9
10
11
12

??


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2001
Posts: 745
M
Member
Joe: Well, I guess I can start out - I know I won't get them all, but the ones that seem to be the most obvious:
1. No cover on the box,
2. No bushings or anti-shorts on any of these connectors,
3. Wrong type of connector used for the AC cable at 9:00 (loose connector, also),
4. No grounding to speak of, except the inadequate backwrap on the older romex at 3:00 - looks kinda like one on the 14-2-G at 12:00 also,
5. Looks like someone trying to pass off a red or orange wire as a white,
6. Might be a wire-fill issue in this little box,
7. Conductors probably not the proper length for extending outside the box,
8. If OC protection for this circuit is 20 amp, the 14-2-G romex is in trouble.

That's about all that's obvious to me. I don't know if it's a violation or not, but I don't have a lot of faith in those wirenut splices.

Mike (mamills)

Joined: May 2004
Posts: 73
R
Member
9. It looks like a 3" octogon box.
10. I heard wire nuts aren't listed to be wrapped with tape.
11. 9:00 locknut looks loose.
8. (continued) The top white wire looks like it says 12 on it so it might be the only properly sized wire on a 20 amp circuit.
12. 6:00 looks like 3/8" FMC which probably isn't a fixture whip.

[This message has been edited by Ralpha494 (edited 08-27-2004).]

Joined: Nov 2003
Posts: 269
E
Member
If that is a 3" box, they have fill violatiions. Also box is not bonded. I don't think clamping the EGC in the romex under the connector counts.


John
Joined: Feb 2002
Posts: 183
N
Member
It's hard to tell, but are those wire nuts rated for that number of wires? They look quite large.

That's a very tight bend on the 14/2 NM.

None of the lines appear properly supported, but the picture doesn't show enough to be sure.

How were those clanps tightened with the screw heads facing the joist like that?


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5