ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#104619 09/10/03 05:10 PM
Joined: Oct 2000
Posts: 2,749
Member
This is a service entrance conductor Drip Loop and has limitations according to the NEC.

What is the minimum distance to the "loop"?

[Linked Image]


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#104620 09/10/03 05:49 PM
Joined: Aug 2001
Posts: 7,520
P
Member
At a quick code clook-up, I would think this is covered by 230.24(B).

Is there a messenger wire there? I can't see one, so I'm guessing that (1) wouldn't apply, and this drop would be covered by either (2) requiring a 12 ft. clearance or (4) requiring 18 ft. if there's truck traffic.

Have I missed anything?

#104621 09/10/03 06:45 PM
Joined: Aug 2001
Posts: 7,520
P
Member
OK, I think I misread that first time. Part (1) applies to the loop so the minimum is 10 ft.

How high is this loop? From an upstretched arm, I'd guess around 8 ft. ?