ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#106729 02/17/05 08:19 AM
Joined: Dec 2000
Posts: 4,294
Member
Because I'll sure be the last one in the pool.

[Linked Image]


[Linked Image]

The owner had a guy replace the timer, and put in a new switch for the pool light. The MC in sealtite goes to a bootleg bathroom that the hack didn't complete.


[Linked Image]

HO says that the hack never mentioned any hazard regarding the pool, which has no bond wire to be found, no GFI for the light, and no ground wire in the conduit to the light.





[This message has been edited by electure (edited 02-17-2005).]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#106730 02/17/05 10:00 PM
Joined: Dec 2000
Posts: 4,294
Member
Here's another one of his remodel projects at the same house.

[Linked Image]


Somehow or another he's got it tied to one of theses switches. This is knob and tube, with no ground.

[Linked Image]

And I'm mad as can be.

#106731 02/18/05 02:59 AM
Joined: Jun 2001
Posts: 642
N
Member
yea. Hacks are every where and they still get the money and run.


ed
#106732 02/19/05 03:18 AM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Electure,
Quote
Because I'll sure be the last one in the pool.
I'll be the rottener egg than you.
You'll be in the pool before me!. [Linked Image]
That's just down-right ludicrous.
Someone should be shot for that standard (if it can be called that) of work. [Linked Image]
In the first pic, is that some sort of an in-ground junction enclosure?.

[This message has been edited by Trumpy (edited 02-19-2005).]

#106733 02/19/05 08:56 AM
Joined: Dec 2000
Posts: 4,294
Member
That's a junction box especially for the pool light. A cord inside of a length of red brass pipe extends down to the wet niche fixture in the pool wall.
I don't know what the Code required at the time this was installed, but currently:
1. It must be 4" above the deck, or 8" above the maximum water level (whichever is higher). {This is not.}
2. It must be 4' or more from the edge of the pool. {This is not}.
3. The conduit must not contain any non-GFI protected wiring. {This does not even have GFI for the light, and there's another circuit running through it to a recp on a patio}.
4. As is obvious, the proper grounding path is non-existent on this mess.