From 8-202 (4) "The ampacity of feeder conductors from a service supplying loads not located in dwelling units shall be not less than the rating of the equipment installed with demand factors as permitted by this code."
So in your case, it is 100%, since you have not listed any electric space heating loads, where you would add them at 75% from 62-116(3).