ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 248 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#102481 04/01/06 08:26 PM
Joined: Dec 2005
Posts: 6
T
teck_ed Offline OP
Junior Member
I have a 100 amp 3 phase service commercial building. The customer wants to open a tanning salon with 4 beds. 1 is 60 amp, 220 vac, 2 @ 20 amp 220 vac and 1 is 30 amp 220 vac. Also some lights, plugs and A/C 20 amp 220 vac. Is the 100 amp 3 phase service big enough? Your help is appreciated.

#102482 04/02/06 09:46 AM
Joined: Jan 2003
Posts: 174
B
Member
Hello ED
Check out section 8 of the code book paying paticular attention to 8-210 and table 14.These will help you determine your service and feeder sizes.

You will need to know the outside dimensions of the building to calculate a basic load and then you will have to add in all of the "special" loads.
When determing the current draw of a paticular machine or piece of equipment make sure you check the " data plate" on the machine for this info and do not go by the breaker size it is connected to.
Hope this helps.

#102483 04/05/06 08:03 PM
Joined: Apr 2006
Posts: 31
M
Member
Is you 100amp 3ph coming in at 600v? Bigrockk is right you should do a building calc. to be sure.

#102484 04/05/06 11:43 PM
Joined: Mar 2006
Posts: 82
B
Member
You dont need to do any demand calculations.

The simple answer is no. Add up the KW for each load and find the total current. Its about 87A just for the beds.

#102485 04/06/06 08:05 AM
Joined: Jul 2005
Posts: 183
J
Member
re bigpapa's reply, you still need to refer to table 14 to establish your basic load, then as 8-210 tells us,"special loads .....based on the rating of the equipment installed with such demand factors as are permitted by this Code." Since your existing service will not be large enough, you still need to get out the calculator to determine the appropriate service feeder size.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5