#101797 05/13/03 04:52 PM
Joined: May 2001
Posts: 378
F
frank Offline OP
Member
Looking for CEC code rules regarding number of wires that can be terminated at a single terminal for breakers,neutal buss bars and grounding bars ect.thanks

#101798 05/13/03 07:29 PM
Joined: May 2001
Posts: 144
T
Moderator
#2-034

Use of Approved Equipment

No one shall use any electrical equipment other than approved electrical equipment of a kind or type and rating approved for the specific purpose for which it is to be employed.

Appendix B

As a condition of approval of certain types of electrical equipment, the manufacturer supplies instructions pertaining to its installation. It is of the utmost importance that the installer closely follow installation instructions supplied by the manufacturer to fulfill the terms of the approval agreement.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

#101799 05/13/03 07:52 PM
Joined: May 2003
Posts: 1,158
Member
6-212 (1)