#101632 04/17/02 08:58 AM
Joined: Nov 2001
Posts: 7
L
Junior Member
Figure 54-922 (Grounding of Antennas) shows a dish being grounded by a #6 to the grounding electrode of a residential application.In a hi-rise commercial application this may not be practical.Is it acceptable to to run the #6 to the nearest panelboard and ground it to the panel with a mechanical lug?
The figure also shows a bonding conductor between the lightning arrester and the panelboard.What size conductor should be used?

Thanks

#101633 04/17/02 07:57 PM
Joined: May 2001
Posts: 144
T
Moderator
Lawrence,

You can install the grounding conductor to the nearest accessible location on the following:

The building or structure grounding electrode system.

The grounded interior metal water piping system.

The power service accessible means external to enclosures.

The metallic power service raceway.

The service equipment enclosure.

Bonding of Electrodes

A bonding jumper not smaller than No.6 copper or equivalent shall be connected between the radio and television equipment grounding electrode and the power grounding electrode system at the building or structure served where separate electrodes are used.
The grounding electrode conductor or the grounding electrode conductor metal enclosures.

Antenna masts must be grounded to the same grounding electrode used for the electrical system of the building. This is necessary to ensure that all exposed, non-current carrying metal parts are at the same potential. In many cases, masts are incorrectly connected to the conveniently located vent pipers, metal gutters, and downspouts. This could create potential differences between lead-in conductors and various metal parts located in or on buildings, resulting in possible shock and fire hazards.