ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 141 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#164511 06/04/07 10:44 PM
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
Can a splice be made in a conduit body for example an LB?

Joined: May 2003
Posts: 1,158
Member
No. But I cant reference a code section They cannot be used for a junction box.

Joined: May 2005
Posts: 984
Likes: 1
G
Member
314.5

There's a VERY limited exception in 314.16C2 that allows it.


Ghost307
Joined: May 2003
Posts: 1,158
Member
Now we need a Canadian Code reference

Joined: Jun 2006
Posts: 613
M
Member
Some conduit bodies are approved for splices. space and wire count is very limited. The body has to have a cubic inch capacity marked on it. There are no specific rules in the CEC that say no but there are none that say yes either. The trick here is, some bodies are approved for splices and many inspectors will respect the Approved use with some evidence suplied from the wholsale and installer.

Joined: May 2002
Posts: 1,716
R
Member
Take note that 314.16(C)(2) not only allows splices in condulets that are marked, it also allows devices to be installed in them.

[Linked Image]

Roger

Joined: Feb 2004
Posts: 74
C
CRM Offline
Member
According the Alberta Standata Code you can't. The code does not permit "conduit fittings" to be used as a junction box. However, in Alberta we have interpreted the term "equivalent device" in rule 12-3000(1) to include "conduit fittings" in special applications (i.e. connection to solenoids, photocells, etc) Wire leads from these devices must be integral to the device. Where the device has a bonding conductor and the conduit fitting has no provisions for attaching a bonding conductor, a separate bonding conductor must be provided in the conduit system to the fitting. The fitting must also comply with the requirements of rule 12-3034 and table 22.

Joined: Jul 2005
Posts: 183
J
Member
I would look at 12-910, and if the fitting is part of the raceway where conductors continue through then I would say no splices because the fitting is part of the raceway. But if the conduit stops at the LB, then you may have a case for splicing with sufficient space as per Mikesh's post.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5