ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 205 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#101561 11/29/01 04:44 PM
Joined: Nov 2001
Posts: 7
L
Junior Member
Concerning CEC Rule 26-746

I'm quoting a commercial job where an 8KW(208V) single phase cooking grill is to be installed.According to 26-746(2)-Every electric heating and cooking appliance rated at more than 1500W shall be controlled by an indicating switch which shall be permitted to be in the circuit or on the appliance except that (a) If the rating of the appliance does not exceed 30A ,an attachment plug and receptacle shall be permitted to be used instead of a switch;and (b) if the appliance has more than one individual heating element,each controlled by a switch,no main switch need be provided.

So where this appliance will draw more than 30A am I required to install a disconnect(with pilot light)? The unit has individual controls for each of the 2 sides of the grill(not sure whether it has pilot lights) so is a range cord and receptacle OK?Can it be hard wired? Am I required to install a disconnect?

Thanks

Lawrence

Joined: May 2001
Posts: 144
T
Moderator
We intend that every electric heating and cooking appliance have an indicating switch, either in the circuit or on the appliance. By an indicating switch we mean one that allows you to visually determine whether the switch is in an “on” or “off” position. If there is more than one individual heating element and each element is controlled by its own switch, no main switch need be provided; an example is an electric range, where each element has its own switch. Up to 30 A, an attachment plug and receptacle are an acceptable means for disconnecting the power to an appliance.

Rule 26-746 Appliances Exceeding 1500 W

(1) Every electric heating and cooking appliance rated at more than 1500 W shall be supplied from a branch circuit used solely for one appliance except that more than one appliance may be connected to a single-branch circuit provided that the following is used:
(a) A multiple-throw manually operated device that will permit only one such appliance to be energized at one time; or
(b) An automatic device that will limit the total load to a value that will not cause operation of the overcurrent devices protecting the branch circuit.

2) Every electric heating and cooking appliance rated at more than 1500 W shall be controlled by an indicating switch which shall be permitted to be in the circuit or on the appliance except that:
(a) If the rating of the appliance does not exceed 30 A, an attachment plug and receptacle shall be permitted to be used instead of a switch; and
(b) If the appliance has more than one individual heating element, each controlled by a switch, no main switch need be provided.

(3) For the purpose of this Rule, two or more separate built-in cooking units shall be considered as one appliance.

Tony Moscioni
Electrical Inspector
© Electrical Safety Authority – 2001