#196470 10/06/10 04:15 PM
NEED 250 94 (2).jpg
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
A 250.94; Why????

Found this recently. Comments Please
1 Comments
Joined: Jul 2004
Posts: 9,935
Likes: 34
G
Member
Because 250.94(1) says
Quote
A set of terminals securely mounted to the meter enclosure and electrically connected to the meter enclosure. The terminals shall be listed as grounding and bonding equipment.


not a service raceway?


Greg Fretwell