ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
Joined: Jan 2014
Posts: 5
R
New Member
Hello all, thank you for taking the time to read, and possibly offer comment.

First of all, the only noticeable side effect of this issue is that my coaxial lines are not able to hold the prober connectivity for more than a few hours because apparently voltage is building up inside their splitters? The internet connection and the tv on-demand connections do not work due to this. Comcast sent many techs to the house to finally arrive at this conclusion. At which point I called an electrician. He checked the grounding of the house, which at the time was the only thing comcast told me to ask for. $125 later, I could say that everything was properly grounded. The electrician did notice voltage mysteriously coming from my outlets and being emitted from the back of all comcast equipment (not isolated to one piece of equipment, and this is withOUT the comcast inbound line connected. So, I get two more electricians out, and they agree something is going on, but they cannot tell me why, or whether it's a hazard (they do not believe it is). Here is the description from the last electrician who was there:

We found 8 volts present on our multi-meter between the ground outlet and the back of the router box, we found the same 8 volts between neutral and the back of the box. The Router is two prone with no ground. We found the same 8 volt issue with the lamp, also a two prong lamp with a metal base. When we grounded the back of the box to the buildings ground through the water pipe the voltage reading went to 0 – on the router and the lamp. When we put an inline amp probe between the rear of the router and the neutral we found no current.
We found the neutral and ground bonded in the panel and to the water system - we recommended adding a ground rod, but we do not believe the lack of a ground rod is causing the issue.
We looked for loose neutrals and loose wiring and we did not find any, we did check and tighten your panel connections.
We believe the voltage is being induced rather than being a direct short, that’s just a theory.

Anyone got any ideas?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2000
Posts: 246
R
Member
A little more info might lead us to the problem. Were both the router box and the lamp plugged into the outlet when the measurements were made? Did the TV guys try a different router? Was anything hardwired to the router (TV, PC, etc...) during the tests?

Joined: Jun 2004
Posts: 1,273
T
Member
This forum is oriented towards professionals.

You are not using trade terms.

Your missive doesn't quite spell out your problem -- other than your system doesn't work correctly.

I'd advise throwing the problem back upon your vendor.




Last edited by Tesla; 01/27/14 10:18 PM.

Tesla
Joined: Jul 2007
Posts: 5
C
New Member
Your problem is not electrical, it is within the cable tv system in your home. Get Comcast back out, have them check ALL of the connectors in the house, on the service drop and at the tap. Look for loose fittings, poorly installed connectors, corrosion between the center conductor and shield and damaged cables. Have them replace anything that is not Comcast approved. Make sure all of the connectors are tight-- a little beyond finger tight (except for the fittings on modems, cable boxes and tv's which need to be finger tight only).


Joined: Mar 2004
Posts: 814
B
Member
Even though the electricians did not find a "loose" neutral I am very suspicious of the integrity of his grounded conductor between the house and the transformer.

Joined: Jan 2014
Posts: 5
R
New Member
thanks for the responses. it's not a comcast issue. We unplugged all comcast lines. Just any piece of equipment (not necessarily a comcast box), and the same 8 volts is read. I assume if this reputable electric company couldn't figure it out, I'm sure my layman's approach to describing the problem here isn't exactly helpful. but thought i would give it a shot. the "issue" was occuring all over the house, not necessarily isolated to one circuit or one piece of equipment.

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Anybody check the earth ground connection at the demark??



John
Joined: Jan 2014
Posts: 1
J
New Member
I'm the writer of the www.NoShockZone.org blog on electrical safety as well as the moderator of the AC Power & Grounding Forum on ProSoundWeb.com magazine, so I'm very interested in what's going on with your grounding problem. At first blush this appears to be an open neutral feeding your house, but not all the pieces fit. Please email your phone number to mike@noshockzone.org so we can discuss this a bit.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Is this an analog meter or a digital meter?

Digital?
Put a 200k resistor across the leads and try it again (the load of a 20,000 ohm/volt analog meter on the 10v scale)
If your voltage goes away, you are chasing a ghost.


Greg Fretwell
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by jmsokol
At first blush this appears to be an open neutral feeding your house, but not all the pieces fit.


An open neutral, usually presents itself as L-N voltages that are not equal.

It is quite common to be able to measure a voltage between a neutral and a ground. This has to do with the voltage drop caused by the load on the circuit.

I am not sure what problem the OP is trying to mitigate.