ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/22/24 10:36 AM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 228 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
i hate to be a forum hog but i have a question that has come up and a few various qualified opinions on the subject would help solve the question.

here is the situation...

given a 3/4 inch run of rigid steel conduit with a 2" tee cut in. re's are used to bush the tee down to 3/4. the only support is a piece of unistrut a foot apart on either side of the tee for this example.. the rest of the run is supported correctly.

the issue is the support of the fitting...i see a code violation here because you would be using a 3/4 inch conduit to support the 2 inch tee...

given that the fitting should contain devices or fixtures you are bound by the same exception as in 370-23 (e)

i realize this has been done for a long time but.....i beleive it was changed in 1996 to eliminate this problem...

thank you for your response

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Oct 2000
Posts: 5,392
S
Member
frodo;
there may be some consideration as to defining this as a 'conduit body' or 'enclosure'.

[Linked Image]

Joined: Oct 2000
Posts: 5,392
S
Member
frodo;
maybe others can comment here, at one time an LB could be either definition. this depended on a termination within it or not. The fill calc ( seen on interior of LB's) were only to be applied to those used for terminations .

Or else we would all be using mogul LB's
(very $$$$$)

[Linked Image]

Joined: Nov 2000
Posts: 2,148
R
Member
This gets a little tricky. 370-23(c) says two conduits screwed into threaded hubs are permitted to support enclosures 100 cubic inches or less without devices or fixtures in the enclosure. The exception tells us that conduit of the same trade size as the conduit body can support the conduit body even if the volume exceeds 100 cu. in.
It is now my opinion that is the volume of the 2" T is less than 100 cu. in. then the 3/4 conduits are permitted to support it.
Don(resqcapt19)


Don(resqcapt19)

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5