ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 391 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#77047 04/18/01 08:53 PM
Joined: Apr 2001
Posts: 1
B
Junior Member
Under section 680-22 (a)1 Would gunite or shotcrete materials be considered a listed encapsulating nonconductive compound & therefore not need bonding of the reinforcing steel?


Bill LaRosa
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#77048 04/18/01 11:29 PM
A
Anonymous
Unregistered
If you have to chance to bond to them, you should probably take it. Just make sure that the steel rods are properly tied (bonded) to each other so that when lightning strikes, there won't be much arcing within the framework.

As for non-conductive: no way!
Both absorb lots of water, form ions, and are very conductive.

This is good in that any current getting to the steel will find a huge footprint to dissipate it into the ground.

When bonding, avoid steel contacting copper or anywhere the water can come into contact with copper and then with steel.

#77049 04/19/01 04:54 PM
Joined: Jan 2001
Posts: 75
G
Member
Billman1,

I have not see a " reinforcing steel efectively insulated by listed encapsulating compound ---".

Call the NRTL who says this encapsulating compound is listed for varification.

Glenn


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5