ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 220 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
What do you guys think about this... Bridgeport makes a line of conduit fittings that used to be U.L. listed as being watertight. Should an inspector have an issue with installing a compression type connector like this outdoors on a conduit riser that is entering the bottom of a panel where it is shielded from direct rain? This might be a trick question...
Why do I ask???
3" diecast Bridgeport EMT/IMC/Rigid connector = $15.
3" Rigid connector = $130 - $180.


Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2004
Posts: 1,273
T
Member
Are you referring to a 'Myers hub' as your Rigid connector?

======

I've never seen diecast connectors ever given a RT listing. Steel, yes.

The newer RT connectors don't differ much: just an additional seal, AFAIK.

I've seen inspectors tolerate Greenfield/ flex ( not Sealtite ) for THWN-2 taps to HVAC condensers -- in residential situations.

In which case, might D.C. S.S. connectors also pass for your application?

BTW, at 3", DCSS fit both RMC/IMC and EMT.


Tesla
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
The connector is a 3" D.C. compression connector that fits EMT/IMC/RGS and is the older style without plastic gaskets.
Since the fitting is under the panel it would be at most an
occasional damp location. I was wondering if would be code compliant to use the die-cast fitting since it is placed so as to prevent moisture from entering. 314.15 only addresses wet locations as far as the U.L. listing requirement is concerned. BTW, The rigid is being used to thwart copper thieves and is overkill for conductor protection in this case.

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Sounds like the local AHJ determines if the underside of the panel requires a watertite connector or not.

Based on his decission, that would be your answer.

Asking him before you spend $$$.





John
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Good advice. I tried calling a couple times but couldn't get through. Double locknut threaded rigid connections under a panel or box outside never seem to raise an eyebrow. The meter panels have weep holes in them anyways so it shouldn't be an issue.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5