ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 228 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#95979 10/27/05 12:11 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
Thsi topic is being discussed in two other threads but here is a different question.
Assume 10 120V circuits each with their own neutral. #12 all in one conduit to a juction box with one ground wire and a ground bus in the junction box. Separate MC from there to the devices, lighting etc.
50% of 25A is 12.5 amps. Does that mean that the branch circuit breaker needs to be less than 12.5 amp? Or just that the connected load can not exceed 12.5 amps?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#95980 10/27/05 12:28 PM
Joined: Sep 2003
Posts: 650
W
Member
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.

Note that for derating based upon number of conductors in a conduit, you get to work from the temperature rating of the wire, even if it is higher than that of the terminations. So you would probably use THHN 90C wire, with an ampacity of 30A, 15A after derating with a 15A breaker.

-Jon

#95981 10/27/05 01:13 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.
Not if the circuit supplies a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
See 240.4(B)(1).
Don


Don(resqcapt19)
#95982 10/27/05 04:38 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I agree Don, if the circuits are feeding receptacles you looking at 10a circuit breakers.


George Little
#95983 10/27/05 09:29 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
OK, so for the receptacle circuits we can not go to the next higher size circuit breaker.
But, if the wire is 90C we can use 30 amp which means 15 amp and a 15 amp receptacle?
(regardless of the termination rating?)

#95984 10/27/05 10:36 PM
Joined: Jan 2004
Posts: 1,507
G
Member
If you have a 90° wire (THHN) #12 AWG using it in a ambient of 86° damp or dry location and derate to 15a due to raceway fill, you could feed 15 receptacles and have a 15a overcurrent device protecting it.


George Little

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5