#95845 10/12/05 11:54 PM
Joined: Sep 2005
Posts: 8
C
cruzer Offline OP
Junior Member
question can you use more than one ground on a ground clamp on the water pipe,does the ground pipe have to be bonded.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#95846 10/13/05 05:30 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Any wire terminal has to be listed for use with more than one conductor if you want to use it that way.

I have not seen ground clamps listed for more than one conductor.

Quote
does the ground pipe have to be bonded

If you mean does a metal raceway enclosing a grounding electrode conductor need to be bonded the answer is yes it does need to be bonded at each end.


Bob Badger
Construction & Maintenance Electrician
Massachusetts