ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#88961 08/17/04 08:40 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
Are the wires feeding from a current transformer considered current carrying conductors? I am wiring up a power factor correction unit and need to feed it with three 2/0's, a ground, and the wires from a CT donut in the main panel. If I install the CT wires in the same conduit as the feeders, will I have more than three current carrying conductors?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#88962 08/18/04 12:25 AM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Would CT secondaries be considered as Article 725 wiring?




[This message has been edited by Bjarney (edited 08-18-2004).]

#88963 08/18/04 09:00 AM
Joined: Dec 2003
Posts: 751
E
Member
Run a separate conduit. Conductors for monitoring of energy usage and the like are control wiring and should be installed as an individual system. It is sloppy procedure to tag along with the power conductors, and may screw up sensitive electronic metering.


Earl
#88964 08/18/04 05:53 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Unless the run is very short, another concern is damage of small conductors by larger conductors in a pull.

#88965 08/23/04 03:36 PM
Joined: Dec 2003
Posts: 751
E
Member
Check out 725.28(B). Are these conductors Class 1?


Earl