ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 506 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#87180 01/28/04 06:49 PM
Joined: May 2003
Posts: 6
B
bobwk Offline OP
Junior Member
I am trying to design a tap ahead of a main breaker for a Hangar door, and NFPA 409 requires a tap ahead of the main. Can an indoor transformer, dry type, 13.2kV pri, 480V secondary be tapped inside the transformer cabinet with 600V insulation wire. Would the tap conductor be required to be rated 15 kV, the transformer is not compartmentalized and is unisulated bus bar on the 480 side to the switchboard. The transformer is up against the main breaker section, all customer owned and metering is not an issue. Any code references would be appreciated.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Dec 2003
Posts: 751
E
Member
NFPA 409:"5.7.2 The power source for hangar doors shall operate on independent circuits and shall not be deenergized when the main disconnect switches for general hangar power are shut off."
Seems to me you could set it up so that you won't have to connect ahead of the main. Why not have a main distribution panel fed by the transformer, one feeder would be to the general hanger panel, a second would go to the hanger doors panel.

Earl


Earl

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5