#84786 05/05/03 08:27 AM
Joined: Apr 2002
Posts: 178
R
Member
I have a question We`re putting in some crouse-hines Illuminator fluoresant lighting in a paint shop new area they are sealed and approved for the area.My question is we have a seal where conduit enters new room and the fixture is sealed If there are no connections in the condulets between two seals can they be standard condulets (t`s and lb`s) or would they also have to be rated for the location. Thanks in advance

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84787 05/05/03 09:11 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Is the area Div 1 or Div 2? If Div 1, then 501.4(A)(3) requires explosionproof fittings.
Don


Don(resqcapt19)