#84361 03/25/03 12:54 AM
Joined: Aug 2002
Posts: 1,081
T
Member
I have a length of 8AWG Type AC cable that at one time ran from the panel to an electric cooktop (since replaced by a natural gas cooktop...)

I guess the cable is considered "8-3" as it has one each of a white, red and black conductor. There is no green conductor. This is not the old "BX" cable with cloth conductors--this is more modern.

NEC 250.4(A)(5) and 250.4(B)(4):
Quote
...The earth shall not be used as the sole equipment grounding conductor or effective fault current path.

Does this mean that the cable can not be used for any new work? While I have no use for it right now, I would hate to toss it if it can possibly be used for something later on.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84362 03/25/03 02:00 AM
Joined: Mar 2001
Posts: 333
S
Member
ThinkGood, if the cable is AC, shouldn't there be a bonding strip inside, that is in contact with the armor? Have you stripped back the armor to see if it is there?


Steve
#84363 03/26/03 12:54 AM
Joined: Aug 2002
Posts: 1,081
T
Member
The bonding strip is there.

I'd like to re-phrase the question some...I know that Type MC has an insulated green conductor for grounding. Does Type AC need a separate conductor for grounding to be compliant with the NEC (1999 and/or 2002), or is the metal armor sufficient?

I thought that the bonding strip is not to be used as a ground. If so, what does it do [Linked Image]

Am I about to get into the "grounding" vs. "ground" vs. "bonding" area? [Linked Image]

#84364 03/26/03 01:02 AM
Joined: Feb 2002
Posts: 840
C
Member
TG, the bonding strip inside type AC cable is there to reduce the reactance (resistance to alternating current) of the cable jacket. Without it, and under fault conditions, the jacket becomes a huge inductor which chokes the fault current, possibly preventing the OCPD from activating. Clear as mud?

Peter


Peter
#84365 03/26/03 08:33 AM
Joined: Aug 2002
Posts: 1,081
T
Member
Sure...an inductor...a duct that takes in the electrons, right? [Linked Image]

Thanks for the explanation.

Still curious, do current (pardon the pun) regs require a separate EGC?

#84366 03/26/03 08:39 AM
Joined: Mar 2001
Posts: 2,056
R
Member
The armor of AC Cable,(0NLY IN CONJUNCTION WITH THE INTERNAL BONDING STRIP), provides an adequate, low impedance, equipment grounding path.
This is not the case with MC cables of the interlocked (spiral wound) armor type. In that case, as CT said, the configuration of the armor will choke the fault current. Therefore, with common MC, the insulated grounding conductor is required to adequately serve as the EGC.



[This message has been edited by Redsy (edited 03-26-2003).]

#84367 03/26/03 11:08 AM
Joined: Aug 2002
Posts: 1,081
T
Member
Thanks again for the clarification!


Link Copied to Clipboard