When running parallel feeders what size equipment ground is used, and do you run this size wire in each pipe?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2001
Posts: 2,056
R
Member
A ful sized ground, based on the OCPD setting(Table 250.122) is required for each conduit. Article 250.122 (C)