in nec 1999 sec 250-94 method [1]
it says you bond the neutral to all service enclosures
my question is : if you anyways need to use bonding l/n,&jumpers at concentrics then whats the point in doing method [1]?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#80870 07/11/02 12:04 AM
Joined: Feb 2001
Posts: 308
S
Member
So a ground fault will complete a circuit by returning through the neutral conductor and trip the breaker by having a low resistance in your circuit. If you don't bond the neutral to the enclosure a ground fault won't have any where to go until something or someone completes that circuit.