#80123 02/28/02 11:33 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Is it legal to have a 20a 120v single recepticle outdoor "not GFI protected", for a spa if the spa has its own GFI built into the plug? Does the recept have to be 5 feet away from the spa?


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#80124 02/28/02 11:36 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Al,

If the Receptacle is outside it has to be GFCI protected period.

Bill


Bill
#80125 03/01/02 11:07 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Thanks Bill, kinda what I was thinking, that makes sense. Would there be any problem with tripping by putting a GFI recept or breaker in since it would be double GFI protected? (The recept and the spa plug both having a GFI on the same 2a ckt).


The Golden Rule - "The man with the gold makes the rule"
#80126 03/01/02 11:10 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
correction to previous message - "20a ckt"


The Golden Rule - "The man with the gold makes the rule"
#80127 03/01/02 11:38 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Al,

I haven't encountered any problems with double GFCI protection like this. These Tubs have been coming with GFI protection in the control panels and some on the cords for years. Look at Hairdryers for a similar situation. Many come with a built-in GFCI (or similar) and don't seem to cause any problems with the Bathroom GFCI.

Bill


Bill
#80128 03/02/02 08:02 PM
Joined: Feb 2002
Posts: 38
H
Member
aldav53
680 !
part VI 680.40 ,,,680.42 then in partII read 680.22(a)(4) that should be enough for ya!