Is it acceptable to run LV conductors in the same conduit with the regular voltage conductors. For instance, undercabinet lighting with the xfmrs in the basement, run to a kitchen above in EMT with the 120v conductors.
I don't think anything is wrong with it, provided the insulation is rated for the highest voltage on all the conductors.
Any opinions?
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
no Opinion Steve, just confusion, would we need to go to 725-26?
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
See Section 300-3(c) Conductors of Different Systems.
[This message has been edited by Joe Tedesco (edited 07-20-2001).]
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Yes yes, but i think the original Q was to address Low-V , as in after a 120/12V X-former. Inasmuch as there is no definition of LV.
|
|
|
|
Joined: May 2001
Posts: 176
Member
|
Sounds like he is putting the ballast for a light fixture in the basement. Check the xfmrs secondary output voltage. It may be higher than you think. Of course, if the xfmr is truly a step down version, then as pointed out by Joe Tedesco, all the conductors in the same raceway, enclosure, or cable must be insulated for the highest voltage.
|
|
|
|