#214916 02/08/15 12:10 AM
Joined: Feb 2015
Posts: 2
M
M45 Offline OP
New Member
for the sake of argument on amperage. i have a T building that needs a feeder to supply 600a for 3 disconnects. the available power source is a 800a H frame service. the feeder has to run over head. any ideas on how to make that happen. any ideas appreciated.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

M45 #214918 02/08/15 11:55 AM
Joined: Dec 2000
Posts: 4,294
Member
Just for some clarification, do you mean a Tee "shaped" building, and a "Square D" 800A H frame service ?

M45 #214919 02/08/15 03:02 PM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Along with the clarifications stated by electure, have you compiled Load Calculations for both the New and Existing Services?

To begin with, I suggest contacting the Local Utility's Service Planner, to discuss this upgrade.
Be sure to have at least a basic Load Calculations Database ready for referencing, too.

If this T.I. Work _DOES NOT_ involve the Service Capacity, then ... ???
(please elaborate)

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Scott35 #214922 02/08/15 08:31 PM
Joined: Feb 2015
Posts: 2
M
M45 Offline OP
New Member
sorry guys it was late when posted

I have a temporary building needing 600a to feed 3-200 panels installed on Temp Buildings. the service to supply the Temp Building is 150' away and needs to be run overhead. The existing service is 800a and not being used because of construction. It has 4-200a disconnects on service not being used. at first I wanted to used the 200a disconnects to supply the 3- Temp building but discovered they are grouping all three together to make 1 building. i now violate 225.30. im just looking for better ideas thsn mine.

M45 #214930 02/11/15 09:01 PM
Joined: Jun 2004
Posts: 1,273
T
Member
You've still got a LOT of missing details...

Run the three temps to three disconnects for TEMP power -- only... skid mounted as necessary... this was the norm for Cashe Creek casino a 350,000 square foot slab job. The final Service was at 21 kVolts.

Construction power is typically only a TRIVIAL fraction of the final Service demand.

No-one in my career starts off with a built out Service early in construction.

So, you do have me puzzled.

(200 Amp NEMA3R panels are chicken feed and they may be used/ second hand as temp construction power.)

Followed by a final new Service/ daughter distribution center, with it feed underground at a suitable point in the construction...

Or have a new Poco transformer pad set next to the new Service.

Temp power rules over-ride long term Service requirements. (Oriented towards firemen/ emergency responders needing to kill power with less than six throws from one spot.)

&&&&&&&&&&

Stay with aluminum conductors as O/H copper is too heavy.

&&&&&&&&&&

An over and under scheme is also possible. I'm forced to guess: is O/H because of a critical access roadway?

( Try horizontal boring -- on a weekend ) Then run the rest of the pipe: cut & cover.)