#199292 02/19/11 01:53 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
In regard to the NEC, could a 225KVA transformer be used to only feed a 200 amp/208 V 3 phase panel with a main breaker. If such a transformer was to be used, then what size primary protection would be needed? Would I wire it as if it were a 75KVA transformer and rate the primary and secondary accordingly? It's a strange request from a customer. In the future he may run the proper size primary and secondary conductors, to get the max out of the 225 KVA trans.
Thanks - Good Day
SJT

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

SJT #199300 02/19/11 05:59 PM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
The way I understand it you use primary protection that protects the transformer and secondary protection to protect the installed secondary conductors.


Greg Fretwell
SJT #199307 02/19/11 11:02 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Need to know how long the Secondary conductors to see if they qualify for the 10' rule mentioned in 240.21(C)(2) or possibly 240.21(C)(3) or 240.21(C)(3). Is it a single voltage secondary qualifying under 240.21(C)(1)? Basically if the xformer is has 225 KVA capacity and you only want to use it at 75KVA there is no problem and the sizing of the primary conductors should be sized to match the secondary load taking in to considration the voltage ratio and maybe an extra 25% would be a good idea to keep the fuses from clearing on start up. There is no need to protect the secondary of the xformer, just the secondary conductors.

Last edited by George Little; 02/19/11 11:04 PM. Reason: Edited for added thought:)

George Little
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Thanks,
I never wired a large transformer to a smaller rating than what it could put out.
Sounds like I'll be OK. I have to check the connection points for the x1, H1, etc. to make sure we use the proper lugs and bolt sizes.

SJT #199667 03/04/11 04:20 AM
Joined: Jun 2004
Posts: 1,273
T
Member
On the economics....

A 225 kVA XFMR is huge. Regardless of the true load it will bleed energy to sustain its magnetic circuit.

Correct sizing would mean a XFMR of 75kVA.

So you're bleeding off 225/75 = 3 times as much parasitic losses as would be nominal.

Do run your calculations.

BTW 3 is the lower bound.

Power cost being what it is -- you'd very likely be much better off scrapping/ reselling the gear and downsizing to a new/used transformer.

Talk to Salinger and others in the used electrical equipment market. You'll have your eyes opened.

http://www.salingerelectric.com/



Tesla