Joined: Oct 2002
Posts: 830
S
Member
Somehow I was under the impression that lay in light fixtures had to be secured by individual wires from a main support above the ceiling. I'm aware that they are to be secured to the "framing members" by screws, rivets, etc....
I'm looking in the 2005 code and that's all I see. Am I missing something? Thanks, Steve....

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Steve:
NEC says what you listed above. Seismic code/building or fire may require independent support. Lastly, plans may require it in the spec; or the ceiling grid mfg may have it in the mfg installation instructions.


John
Joined: Oct 2002
Posts: 482
Z
Member
HotLine's got it right, especially out here on the West coast. Your building and seismic codes dictate much more of the overhead support requirements than your NEC and electrical inspector.

If there is any question about the requirements in your area, contact your AHJ as early in the job as possible to avoid going back for a red tag from someone you don't expect.

Good Luck!

Joined: Mar 2003
Posts: 849
Y
Member
300.11 (A) 1(Fire -Rated assemblys ) 300.11 (A) 2 Non-Fire -rated. Handbook covers it quite well,
also 410.16.
More or Less says UNLESS ceiling assembly has been Tested and Listed for that use. Support wires are required & must be marked by color or tagging.