ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 263 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#101307 03/04/07 07:37 PM
Joined: Jan 2007
Posts: 59
D
Member
As I said in an earlier post a while ago,we are slow at work right now so me and my buddy find ourselves going on other peoples jobs.I am about finished hot-checking this house now on Pensecola Beach where among other things,the sub feed to the panel upstairs is 2 conductor and grond to main lug panel on breaker in service downstairs....Anyone see a problem here?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#101308 03/04/07 09:51 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I don't see a problem with it as long as the wires are protected at their ampacity and all they need is single voltage circuits. Hopefully one of the insulated conductors is the "grounded" conductor and one is the "grounding" conductor. I see that combination sometimes when a contractor has to refeed an existing subpanel after relocating the Service to accomodate a room addition. If they can't get to the existing panel with SER they wil use the existing SE cable and convert the old panel to 120v. This means connecting both bus to the same side of the line. Kinda hookey and maybe wouldn't pass for new construction but it's safe IMHO. It does potentially put the system in an unbalanced state but one could compensate for this at the main service.


George Little
#101309 03/04/07 09:54 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Sounds like your down there in gfretwell area of the country so I'm sure he'll have something to add to this issue.


George Little
#101310 03/05/07 10:53 AM
Joined: Sep 2003
Posts: 650
W
Member
George described the _right_ way to do this. If you have 2 insulated conductor and a grounding conductor, then you can feed a 120V subpanel. This means one insulated 'hot' conductor, one insulated 'grounded' conductor, and one bare equipment grounding conductor.

Just to make it very explicit: if this is a 120/240V panel, where the bare conductor is being used as the grounded current carrying conductor, then you have clear violations of code.

-Jon

#101311 03/05/07 07:20 PM
Joined: Jan 2007
Posts: 59
D
Member
Yeah,Ikindo posted this to bore you:}It is 120-240 but I thought I would get some of you guys input...I don't wanna start anything but I wonder where the line is drawn sometimes.I would have defintly changed it...I also wonder if my bosses ever had it drawn to their attention.I guess I will MODESTLY mention it

#101312 03/05/07 09:45 PM
Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
Quote
If they can't get to the existing panel with SER they wil use the existing SE cable and convert the old panel to 120v. This means connecting both bus to the same side of the line.

This gets a little problem if there are any shared neutrals between circuits.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5