Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Pool pump motors aren't fed with a GFI breaker, but spa's are, why is that? Do I need to feed an underground aquarium with a GFI breaker? If so, does it have to be fed from the 125a sub-panel, to a 60 amp sub-panel that will control the motors, or just 1 GFI breaker for each pump motor?


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I think it is an oversimplification to say you GFCI spas and not pools.
This started with the "skid pack" spa that was assembled in a factory and seldom inspected by anyone. NFPA required that to be GFCI. Field assembled units were not required to be GFCI. As code cycles marched on more and more got the GFCI requirement. Now it is only 3 phase or very large field assembled spas that are not GFCI. Pools are also increasingly required to be GFCI. If it has a cord and plug, it has to be GFCI. I think the same will be true of your fish tank. In 2005 this is article 682.


Greg Fretwell