Is there a code requirement for the distance that a incandescent type A-lamp would be required to maintain from combustible surfaces such as wood?

For instance, if a 60watt A-lamp, screwed into a keyless lampholder in a basement of a dwelling, was within an inch of a wooden rafter, this would seem to be a hazard.

410.5 gives me some guidance, but is there any other clear guideline that would specify distances from combustible material for type A-lamps?

shortcircuit

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#96543 12/05/05 09:35 PM
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
Depends on the bulb used...do you have a thermocouple handy?

If I remember correctly, industry standards set 140 degrees F as the maximum temperature a fixture can cause on a "flamable" surface.

#96544 12/05/05 10:17 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
"within an inch of a wooden rafter, this would seem to be a hazard." - Yep....bulb to the side or below, I think it would be too close.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#96545 12/05/05 11:00 PM
Joined: Dec 2005
Posts: 64
J
Member
410.5 Luminaires (Fixtures) Near Combustible Material.
Luminaires (fixtures) shall be constructed, installed, or
equipped with shades or guards so that combustible material
is not subjected to temperatures in excess of 90°C
(194°F).