S
Member
Most variable speed drive I have seen use a shielded cable, low voltage ac or dc to control a variable speed drive remotely. Is it possible to use THHN and pull it in with line voltage 277 & 110 to control a variable speed drive remotely? Or is this a code problem?

Thanks

edited to remove excess spaces and improve readability

[This message has been edited by resqcapt19 (edited 11-21-2004).]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2000
Posts: 2,148
R
Member
If you are asking about the speed control circuit, it is likely an Article 725 Class II circuit and is not permitted in the same raceway or cable with the power conductors.
Don


Don(resqcapt19)
Joined: Nov 2004
Posts: 14
S
Member
Looks like I will be running some conduit for that control circuit then.
Thanks Don for the quick reply.