ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jun 2004
Posts: 2
J
JBO1960 Offline OP
Junior Member
What is the minimum concrete coverage for conduits/raceways installed in building floor slabs and where is it referenced in the NEC.


James Wright
Project Enginner I
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2003
Posts: 4,391
I
Moderator
0"

Table 300.5


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Jun 2004
Posts: 220
T
Member
2" according to t300-5 note #2
" raceways approved for burial only where concrete encased shallrequire concrete envelope not less than 2" "

Joined: Jan 2003
Posts: 4,391
I
Moderator
Trekkie, That note only applies to raceways that are only approved for direct burial with concrete encasement.

That note does not apply to RMC, RNC, IMC etc. Those methods can be direct buried without the need of concrete, those methods only need 0" of cover under a building. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Jun 2004
Posts: 220
T
Member
I always thought the 0" meant that the wiring method could't be used in the particular situation. What is considered " under a building"? we are talking about in a slab not under it. wouldn't that be all other locations?

Joined: Jun 2004
Posts: 2
J
JBO1960 Offline OP
Junior Member
It is my understanding that Article 300.5 "Underground Installations" and Table 300.5 was specifically for conduits installed underground or under slabs. No where does the code state for conduits installed "within" floor/ceiling slabs. If you are refering to table 300.5, "All locations not specified below" then for RGS would need to have 6" cover in a slab.
This cant be right.


James Wright
Project Enginner I
Joined: Aug 2001
Posts: 599
N
Member
OK how about 300.6(B). There is no cover requirement but it does specifically allow suitable raceways "in" concrete.

Joined: Dec 2003
Posts: 751
E
Member
The building code (2003 IBC) has this to say:
"1906.3 Conduits and pipes embedded in concrete.
Conduits, pipes and sleeves of any material not harmful to concrete and within the limitations of ACI 318, Section 6.3, are permitted to be embedded in concrete with approval of the registered design professional."

And, generally the cover requirements are the same as for rebar:

TABLE 1907.7.1
MINIMUM CONCRETE COVER

CONCRETE EXPOSURE MINIMUM COVER
1.Concrete cast against and permanently exposed to earth 3"

2.Concrete exposed to earth or weather
No. 6 through No. 18 bar 2"
No. 5 bar, W31 or D31 wire, and smaller 1½"

3.Concrete not exposed to weather or in contact with ground
Slabs, walls, joists:
No. 14 and No. 18 bars 1½"
No. 11 bar and smaller ¾"
Beams, columns:
Primary reinforcement, ties, stirrups, spirals Shells, folded plate members: 1½"
No. 6 bar and larger ¾"
No. 5 bar, W31 or D31 wire, and smaller ½"

Engineers and concrete contractors look at embedded conduit as a necessary evil. Conduit doesn't provide much in the way of strength and can often weaken the concrete if not installed correctly. Keep your embedded conduit runs at least 2 inches back (or structural engineer's requirements) from the finish to avoid "pop-outs", and allow space between the conduit and the rebar for the aggragate to flow all around both. If installing in floor slabs, install the conduit under the wire mesh.