ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 504 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#87349 02/18/04 10:04 AM
Joined: Mar 2003
Posts: 849
Y
Member
Question
formula for voltage drop
example 4160 mtr. distance 475 ft. full load amp (500hp) 70 . Copper wire.
22.3x distance x amps divided circular mil of cooper wire.
22.3x475x70=741477
#4=41740area cir. mills
741477divided by 41740=17.76 voltage drop
4160x3%=124.8
hows it look guys????

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#87350 02/18/04 05:16 PM
Joined: Dec 2003
Posts: 751
E
Member
I prefer the formula VD = 1.73xLxIxR/1,000. The R is resistance per 1,000 feet from Table 9 of Chapter 9. L is the distance from the source to the load in feet. Note that the impedance varies with the pipe type. But is not significant except with higher ampacities. For your parameters using PVC conduit I get: VD = 1.73x475x70x0.31/1,000 = 17.83 volts. Pretty close.
Use 2 instead of 1.73 for single phase.

Earl