ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 160 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#85539 07/12/03 07:29 PM
Joined: Jul 2003
Posts: 1
R
Ron100 Offline OP
Junior Member
LANDSCAPE LIGHTING USING PVC: 120 volt 20 amp GFCI protected: 12 inches (plus) depth: Lights in lawn aside concrete walkway:

Question: Do sweeps and risers to boxes at grade need to be rigid metallic (galvanized)?

Many thanks, Ron

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#85540 07/12/03 09:06 PM
Joined: Mar 2001
Posts: 2,056
R
Member
Are you referring to possible physical damage? per 352.12(C)?

#85541 11/04/03 09:07 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I Can't use PVC where I'm at, (Galvy Only!)but out of town in other cities in my area... Direct burial romex, sleaved with PVC, or just PVC all the way. Then, I dig, ( Or, should I say, have some of the generals guys dig. )a post hole at each light location. Mount my box to a pressure treated 2x4, with a 45 at the top. Looks nice, like it was supposed to be there! Then have the general fill the post hole with concrete, around the 2x4, and the sleeve or conduit. Once the concrete is dry, it is a solid unit! Sounds like a bit too much, but practically in-destructable. You have to run over it with a truck!

But, to answer your question. You still need to support the box, and it depends on what is allowed in your area. Call your Inspector.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#85542 11/06/03 06:56 AM
Joined: Oct 2000
Posts: 5,392
S
Member
Q on that e57, could each box be buried ?

#85543 11/06/03 07:15 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Ron if you want to support a box holding a fixture with the raceway it must be with rigid and you must follow the rules of 314.23(F)

Quote
314.23(F) Raceway Supported Enclosures, with Devices, Luminaires (Fixtures), or Lampholders. An enclosure that contains a device(s) or supports a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 450 mm (18 in.) of the enclosure.

If you want to stay with PVC you will have to support the box some other way.

And then of course the inspector could get you on exposed to physical damage as Redsy has pointed out.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5