1 members (Scott35),
534
guests, and
35
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
I just wanted to mention that I recently heard that Murray has somehow redesigned their Panelboards and claim that other breakers tested and classified for use in the older panels can not be used in newer Murray Panels.
Has anyone else heard this?
Bill
Bill
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
Hello Bill
This is a very interesting situation. I myself am a little confused over this issue, because of conflicting info that is available. I have some info in my office, I am at home, that I will dig up later about this. I will say that I have spoke to both UL and individual manufacturers about this subject and I cannot do justice to this subject until I get the info from my office.
Pierre
Pierre Belarge
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Bill, If Murray has redesigned the bus in their panels, then neither the listed nor classified breakers made for the older panels would be permitted to be used in the new panel. If they made a big enough change to be able to patent the new bus and breaker design, they will be able to prevent any one from making "classified" breakers that fit the new panel. I believe this is exactly what happened with the Square D QO breakers. That bus design is unique and was patented by Square D. There were no third party breakers available for that panel for many years. Now there are "classified" breakers that can be used in the Square D QO panels. I assume that this is because the patent has expired. Don
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
Pierre,
Thanks, I look forward to seeing what you have come up with on this issue, it is very confusing.
Don,
I don't know specific details but heard that an official letter/memo would be coming out from them about it.
Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
This issue of "classified breakers" is one of the reasons that I believe that 110.3(B) only applies to the information in the actual "listing and labeling" and does not include "manufacturer's instructions" as all manufacturers state that you can only use their breakers in their panels> Don
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 2,723 Likes: 1
Broom Pusher and Member
|
Scott " 35 " Thompson Just Say NO To Green Eggs And Ham!
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
Here is the last memo (from 2001) that was passed around about this:
Bill
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
All of the breaker manufactures have published statements like that. Yes, they may be able to void the warranty, but that does not make the use of "classified" breakers a code violation. The "warranty" issue is a legal one, but I have been told that it can be voided if a contractor installs the classified breaker, but not if the end user of the panel installs the "classified" breaker. (is our resident attorney still around?) This is a perfect example of a "manufacturer's instruction" that 110.3(B) does not require you to follow. Don
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
conversely FPE fires continued to have our monitoring agencies backpeddle ,despite being installed via listed instructions....
|
|
|
Posts: 421
Joined: September 2005
|
|
|
|