ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 236 guests, and 31 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#86048 09/03/03 10:59 AM
Joined: Mar 2003
Posts: 15
B
boxford Offline OP
Member
What article in the NEC states that you can only utilize a circuit breaker up to 80% of its capacity?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#86049 09/03/03 11:33 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
210.19(A)(1) & 215.3 provide limits for overcurrent protection of continuous loads


Ron
#86050 09/04/03 09:41 AM
Joined: Jan 2002
Posts: 163
D
Member
(1999) 384-16(d) - Continuous Load
'The total load on any overcurrent device located in a panelboard shall not exceed 80% of its rating where, in normal operation, the load will continue for 3 hrs. or more.'

(2002) - In 2002 this section was deleted.[Proposal 9-107, ROP] It was contended that rules in 210.19(A), 210.20(A), and 215.3 cover this issue and this wording was unnecessary.

#86051 09/04/03 12:46 PM
Joined: Mar 2003
Posts: 15
B
boxford Offline OP
Member
Thank you very much I really appreciate it.

#86052 09/12/03 08:35 AM
Joined: Aug 2003
Posts: 2
J
Junior Member
Most small molded-case breakers are only rated for 80% of their nominal rating. Larger frame molded case breakers can be specified as "100% rated" but will cost more. Best to check with the manufacturer.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5