|
1 members (Scott35),
499
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2000
Posts: 15
OP
Member
|
In 210.12(B) it says -All branch circuits that supply 125v, single phase, 15 and 20 amp OUTLETS in berooms shall be protected. My question is is a switch for a light fixture considered an outlet?
|
|
|
|
Joined: May 2001
Posts: 552
Member
|
Article 100 Definitions Outlet-A point on the wiring system at which current is taken to supply utilization equipment. Not by definition,but if the switch is supplying a fixture in the bedroom it would have to be on the AFCI circuit.
BTW-- Where is Little Elm?
[This message has been edited by txsparky (edited 02-10-2003).]
Donnie
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Actually 210.12 (2002 NEC) requires the AFCI to "provide protection for the entire branch circuit". It was the '99 code that referred to the "outlets"
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
I still want to konw where I can find an outlet that is rated 125 volts, 15 or 20 amps. Don
Don(resqcapt19)
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Don, Check the supplier that provides the 3 phase 115 volt motors listed in Table 430.150!
|
|
|
|
Joined: Oct 2001
Posts: 597
Member
|
Following on what txsparky said, and a comment I just saw in Mike's latest newsletter, since a switch is not an outlet (definition). . .if the switch inside the bedroom is controlling only load outside the bedroom (say, the outdoor flood lighting, or the closet light), then the branch circuit the switch is in does not require AFCI protection.
Al Hildenbrand
|
|
|
|
Joined: Dec 2000
Posts: 15
OP
Member
|
thanks guys...first, the 2002 does refer to 15 and 20 amp outlets 210.12(b). Second, little elm is in the DFW 10 miles from Frisco and about 25 miles north of Dallas. Fastest growing city in texas by percentage population under 50,000. Thanks for the posts...helped me win an arguement.
|
|
|
|
Joined: Jun 2002
Posts: 58
Member
|
And part of the array of outlets to be protected are the Smokeys (210-8). Can anyone in CMP#2 tell me why?
|
|
|
Posts: 240
Joined: March 2005
|
|
|
|
|