#79180 11/30/01 12:15 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
From my understanding, with this rule you don't need to fuse the feeders of a sub panel less than 10 ft. There is usually no extra lugs to tap off a main panel, so you have to fuse them with a breaker anyway. Am I thinking right?
(Just thought about the 25ft tap rule, have to look it up).


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#79181 12/01/01 02:34 PM
Joined: Dec 2000
Posts: 4,294
Member
There are so many variables in this question that it's hard to respond.
{240.21(B)(1)}If you have a conductor to a subpanel less than 10'long, that conductor does not have to be protected at its ampacity. It can be 1/10 of the ampacity of the OCPD that feeds it.
{408.16}The subpanel, however cannot be protected by a larger OCPD than its rating, so it would have to be protected by a main breaker or a OCPD in the main panel if the sub's rated at less than the main panel's OCPD.

#79182 12/05/01 10:01 PM
Joined: Dec 2001
Posts: 4
B
Junior Member
aldav53, they do make panels that have a main breaker at the top for the feeds and have lugs at the botom of the panel to feed a sub panel which is a main lug panel sitting next to the main panel, so in a way the tap is just a continuation of the buss bars