ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 524 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#154156 06/15/04 10:34 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline OP
Member
Intuitively I require a positive means of electrical disconnect on the secured side of a door that has a magnetic lock. So on each door (on the inside secured side), there is a motion detector and push button wired to provide automatic and manual release of the mag lock.
Is the manual release required by code?


Ron
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#154157 06/15/04 11:13 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline OP
Member
I should also clarify that this is a door exiting a electrical room within the building.
I have found 1008.1.3.4.3 pertaining to entrance doors, but that wouldn't apply to an electrical closet.


Ron
#154158 06/16/04 01:16 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Hi Ron. Remember that as defined, anywhere in the building is considered to be a means of egress, so all doors apply to your stated code provision.

Notice also a huge change in the 2003 edition of the IBC that is found in the last sentance of the first paragraph of 1008.1, which further validates the requirement by saying that if though the door isn't required (for egress width), it still must comply with the requirements of section 1008.
[Linked Image]


Ryan Jackson,
Salt Lake City
#154159 06/16/04 01:49 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline OP
Member
I thought it wouldn't apply since it says entrance doors which is not defined in the IBC/IFC. I considered an entrance door as the exterior entrance door or entrance to a tenant space, not an electrical room.


Ron
#154160 06/19/04 07:14 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Spotted this, and remembered reading some commentary for the 2002 NEC. 110.26 C 2 (If it applies to your situation... If so it would have to be of the panic touch bar type.)'99 doesn't have it.

"For the 2002 Code, a new requirement provides for the installation of panic or push-type hardware on personnel door(s) used for egress from electrical rooms containing large electrical equipment (such as switchboards, panelboards, and the like that are over 6 ft wide and rated 1200 amperes or more).
This new requirement affords safety for workers exposed to energized conductors by allowing an injured worker to safely and quickly exit an electrical room without having to turn knobs or pull doors open."


Mark Heller
"Well - I oughta....." -Jackie Gleason

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5