ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 515 guests, and 37 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Apr 2007
Posts: 3
B
New Member
What method [Or type of equipment] does your company use to "THUMP" your underground cables? We use a Cable Dynamicis/Baur for "Thumping and Radar"
Is there a newer technology for locating the fault in the conductor/cables?

Arc Flash PPE Clothing, LOTO & Insulated Tools
Joined: Dec 2005
Posts: 869
Likes: 4
R
Member
We use a BAUA surge generator STA 1100 or thumper.
This method is used to locate faults within an armoured cable or for faults between phase to phase and phase to screen.
We use a Biddle stereo microphone, and magnetometer set for pinpointing the fault.
It pays, prior to thumping to mark out the cable route with a Radiodetection or other cable locator. especially in noisy areas.
Accuracy is within one meter of the fault.

For ground faults in single core cables we use the POPIE ( pool of potential in earth ) method.
This is basically a pulsing HV dc supply, which is short circuit proof.
A testcurrent of about 60 mA is enough to pinpoint the fault within 5 cm. (2 inches)
A balanced µA meter with two probes is used for the pinpointing.


The product of rotation, excitation and flux produces electricty.

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5