ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 205 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 2,723
Likes: 1
Scott35 Offline OP
Broom Pusher and
Member
In regard to the Thread Size Feeder?, located at the NEC Forum Area, I have compiled and attached (4) Panel Schedules for example descriptions.

Basic Descriptions:

a. System = 208Y/120V 3 Phase 4 Wire,
b. Panelboard(s) are 30 Space, 200 Amp, 3 Phase 4 Wire, MLO,
c. Loads are as described in the Thread, and per each Schedule's notes.

Post #1 of 2:
Example #1 (PSCHED 1M): 30 Space Panelboard with L-L VA figured as Amperes x 208 / 2; Neutral Load from L-N Circuitry only.

and,

Example #2 (PSCHED 2M): 30 Space Panelboard with L-L VA figured as Amperes x 120; Neutral Load from L-N Circuitry only.

--Scott (EE)


Attached Images
Attached PDF document
PSCHED_1M_ECN_121229.pdf (185.58 KB, 164 downloads)
Attached PDF document
PSCHED_2M_ECN_121229.pdf (185.61 KB, 187 downloads)
Last edited by Scott35; 12/29/12 11:08 PM.

Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Oct 2000
Posts: 2,723
Likes: 1
Scott35 Offline OP
Broom Pusher and
Member
Post #2 of 2 - examples #3 and #4:

In regard to the Thread Size Feeder?, located at the NEC Forum Area, I have compiled and attached (4) Panel Schedules for example descriptions.

Basic Descriptions:

a. System = 208Y/120V 3 Phase 4 Wire,
b. Panelboard(s) are 30 Space, 200 Amp, 3 Phase 4 Wire, MLO,
c. Loads are as described in the Thread, and per each Schedule's notes.

Post #2 of 2:
Example #3 (PSCHED 3M): 30 Space Panelboard with L-L VA figured as Amperes x 208 / 2; Neutral Load from ALL Circuits.

and,

Example #4 (PSCHED 4M): 30 Space Panelboard with L-L VA figured as Amperes x 120; Neutral Load from ALL Circuits.

--Scott (EE)

Attached Images
Attached PDF document
PSCHED_3M_ECN_121229.pdf (185.98 KB, 117 downloads)
Attached PDF document
PSCHED_4M_ECN_121229.pdf (185.97 KB, 120 downloads)