1 members (Scott35),
428
guests, and
9
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Aug 2002
Posts: 1,081
OP
Member
|
http://www.news.com.au/common/story_page/0,4057,6699117^1702,00.html
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
ThinkGood, It's not the way that I want to leave this Earth!. Makes you think though, about your next pit-stop at the side of the road, at night, of course!.
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Presumably there was some current flowing to ground on that "uncovered ground line." A tragic demonstration on voltage gradients.
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Was this a single wire earth return system? Don
Don(resqcapt19)
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Bjarney, Over here, that current is a maximum of 8 Amperes, it's normally a lot lower than that though!.
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
Mike, at the time I spoke to an engineer at the utility in Calgary who explained that a government inspector required periodic {annual or ?} tests of ground resistance at the remote end. The utility would also run a span between the last two poles {at the remote 15kVA pot} and bond ground electrodes at both poles, for reliability’s sake.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Bjarney, That sounds like a real good idea!. The main down-fall of SWER systems, is what would happen if the Earthing is faulty. It's best to have as lower Earth resistance as possible.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Bjarney, ECP 31, over here calls the need for tests to be performed at 9 monthly intervals. The test value shall be less than 2000 ohms(?!). This value seems awfully high!!.
|
|
|
Posts: 30
Joined: January 2013
|
|
|
|