Discussion:
1999 NEC, Section 310-4, Exception No. 4: Under engineering supervision, grounded neutral conductors in sizes No. 2 and larger shall be permitted to be run in parallel for existing installations.
FPN: Exception No. 4 can be utilized to alleviate overheating of neutral conductors in existing installations due to high content of triplen harmonic currents.
This Question is for any engineer who can give the steps needed to accomplish Code compliance:
Please give the answer to a situation where an existing EMT, using 4 #2 AWG THW Copper conductors will require a larger neutral, such as another #2 AWG THW added to make 5 wires in an existing 1-1/4 inch EMT.
How will your supervision be applied to this type of installation?
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
probably with some long winded explanation of natural grey....
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
The engineering supervision exception allows parallel neutrals for a wire size smaller than the usual 1/0 minimum for parallelled conductors. It does not allow for increased condiut fill. An additional #2 THW in this conduit will exceed the allowable fill. 1 1/4" conduit allows .598 sq.in. fill. It currently is filled to .533 sq.in., and therefore maxed out for #2. This is a good example of someone following the minimum code requirements. 1 1/2" conduit would of been easier on the pull, also. But, hindsight is 20-20, and I can't say I blame the installer. Is this a theoretical, or real instance?
|
|
|
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
Sparky:
Yes, I agree, you are probably correct, and the new 2002 NEC removes the word "natural" wherever it described the grounded conductor.
Redsy:
Just a scenario, and yours was a good reply -- and the first one that gives us a good reason to be concerned about "who" does the supervising!
Also, Chapter 9, Table C1 on page 585 in the 1999 NEC shows where only 4 THW are allowed in the 1-1/4 inch EMT, and where 6 are allowed in the 1-1/2 inch EMT.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
There would not be this 'engineering conflict' to simply upsize the noodle....
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Better yet, there would be little concern if it were in fact fed via 1 ph.
|
|
|
|
Joined: May 2001
Posts: 176
Member
|
Joe brings up a good question. What constitutes "Engineering Supervision"?
Every project I work on here at work is under the direction of a Registered Professional Engineer. I call that engineering supervision. However, if I were out there pulling wires, etc. as some of you are, then what is engineering supervision? Inspectors aren't required to be Registered Engineers in this state, perhaps in other states. As a field person, do you need to hire an engineer when necessary? How do you confirm that you have done so? Does the engineer sign off on something?
Just a few questions that come to mind.
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Originally posted by WARREN1: Joe brings up a good question. What constitutes "Engineering Supervision"?
Every project I work on here at work is under the direction of a Registered Professional Engineer. I call that engineering supervision. However, if I were out there pulling wires, etc. as some of you are, then what is engineering supervision? Inspectors aren't required to be Registered Engineers in this state, perhaps in other states. As a field person, do you need to hire an engineer when necessary? How do you confirm that you have done so? Does the engineer sign off on something?
Just a few questions that come to mind.
As a daytime employee of a chemical plant, I report directly to a chemical engineer. I have never used the "Engineering Supervision" clause, and the assumption could be made that an E.E. is required. However, chemical engineering seems to encompass many physical disciplines, and I have discussed many electrical & code issues with him.
|
|
|
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
|
|
|
|