I am working with a portable AC unit that needs to keep a small computer room cool. If the power goes out to the building the AC will shutoff and won't comeback ON automatically.
My question is: can i bypass (jumper) the main ON/OFF switch so once the power turns back ON the AC will do as well.
Or is there a better solution?
The cost of a single central AC just for that room is way too expensive for this small start up company.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
Is the on/off switch a momentary switch? If not, then leaving the switch in the on position should restart the unit when power returns.
Aside from the technical issues, do you really want to modify the equipment? I would think the LIABILITY INSURANCE would be rather significant if something did not go well.
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
Is the on/off switch a momentary switch? If not, then leaving the switch in the on position should restart the unit when power returns.
Aside from the technical issues, do you really want to modify the equipment? I would think the LIABILITY INSURANCE would be rather significant if something did not go well. The switch is a momentary.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
Contact the manufacturer. There may be some sort of user menu where you can set the machine to start up after a restoration of power. The same idea but different application, as the sleep timer on a TV set.
Can the A/C be connected to a home automation system? If so, perhaps the connection point allows remote operation.
Does the A/C unit use a remote control? Perhaps the remote could be hacked?
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I think Larry's first response is the only real answer for you. See what the manufacturer says. You really want to be using the approved solution. I am sure you can jumper something out to make it go but that might be outside the scope of your insurance.
Greg Fretwell
|
|
|
|
Joined: Feb 2003
Posts: 368
Member
|
Small UPS depending on how long the power is going to be off?
|
|
|
|
Joined: Aug 2002
Posts: 402
Member
|
Actually being a AC it need a large UPS. Contact the manufacturer and see if they make an 'auto restart' kit.
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
I contacted the manufacturer they could not help me. The unit doesn't have an auto ON function. I think i will push them to go to a small central AC unit just for that room.
Too bad the building owner doesn't allow a wall mounted unit.
Thank you all for your replies.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Are you samiliar with what is called a 'mini-split' system?
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Niko: You said a 'small computer room'?
Is that room a 'IT' classified room? (Article 645)
I suggest that you check into that Article. As you said a 'small start-up' company, but your building dept may have issues with that 'room'.
It all depnds on what it is 'called' and by whom.
A seperate system works in an 'IT' room by Art 645, but there qre other requirements.
John
|
|
|