#58063 10/28/05 12:20 AM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
There was recently a thread that dealt in part with this topic, but for the life of me I cannot find it. My question is: WHAT IS THE DEFINITION OF A TAP CONDUCTOR? I find it nowhere in the NEC. More specifically, when you terminate a #8 copper in a box for a raqnge recept, can you pigtail the grounds to a smaller AWG? Is this a "tap"?

#58064 10/28/05 08:59 AM
Joined: Aug 2003
Posts: 1,374
R
Moderator
You will find your definition in 240.2.

Also, what you describe is not a tap, it is an undersized equipment grounding conductor [Linked Image]


Ryan Jackson,
Salt Lake City
#58065 10/28/05 03:27 PM
Joined: Jun 2004
Posts: 1,273
T
Member
Tripp, you're hunting for table 210.24....

Also study 240.5 particularly 240.5(2)

Also study 210.19 (A)(3) exceptions #1,#2

Also study 210.19 (A)(4) exception #1 (c)

These tap conductors are limited to 18 inches.


Tesla