ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#209806 04/29/13 01:49 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
A typical hydraulic elevator with a 20HP code F motor. 72A running and 166A start up.
The question is - is the 166A start up just the normal motor start current or is it something that should be taken in account for:
1. circuit size?
2. generator sizing?
3. voltage drop?

cgw #209807 04/29/13 02:45 PM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
The biggest issue of the 3 is the generator. Other than that I would just design to 125% of the FLA. Voltage drop would be an issue if the branch circuit is very long. There are a number of voltage drop calculators around but if this is existing, it is hard to beat simply measuring the voltage at each end. Just be sure the motor is running when you check the line side end to get an accurate measurement of that leg.


Greg Fretwell